Intermediate Average Arcing Current Equation and Calculator per IEEE 1584-2018
Electrical and Electronics Design and Engineering
Intermediate Average Arcing Currents Equation and Calculator per IEEE 1584-2018
This calculator and equation will determine the arcing current at the open circuit voltage. Requires premium membership account to access calculator.
Arc Flash Hazard Calculations Procedure and Considerations For Medium Voltage System
Preview: Intermediate Average Arcing Currents Calculator per IEEE 1584-2018
Iaoc_Voc = Average RMS arcing current at the voltage level
Ibf = Bolted fault current for three-phase faults (symmetrical rms) (kA)
G = Conductor gap distance between electrodes (mm)
k1 to k10 = coefficients provided in Table A given below
lg = log10
VCB: Vertical conductors/electrodes inside a metal box/enclosure
VCBB: Vertical conductors/electrodes terminated in an insulating barrier inside a metal box/enclosure
HCB: Horizontal conductors/electrodes inside a metal box/enclosure
VOA: Vertical conductors/electrodes in open air
HOA: Horizontal conductors/electrodes in open air
Table A - Coefficients for Equation
E.C. / Voc
k1
k2
k3
k4
k5
k6
k7
k8
k9
k10
VCB
600 V
−0.04287
1.035
−0.083
0
0
−4.783E-09
1.962E-06
−0.000229
0.003141
1.092
2700 V
0.0065
1.001
−0.024
−1.557E-12
4.556E-10
−4.186E-08
8.346E-07
5.482E-05
−0.003191
0.9729
14300 V
0.005795
1.015
−0.011
−1.557E-12
4.556E-10
−4.186E-08
8.346E-07
5.482E-05
−0.003191
0.9729
VCBB
600 V
−0.017432
0.98
−0.05
0
0
−5.767E-09
2.524E-06
−0.00034
0.01187
1.013
2700 V
0.002823
0.995
−0.0125
0
−9.204E-11
2.901E-08
−3.262E-06
0.0001569
−0.004003
0.9825
14300 V
0.014827
1.01
−0.01
0
−9.204E-11
2.901E-08
−3.262E-06
0.0001569
−0.004003
0.9825
HCB
600 V
0.054922
0.988
−0.11
0
0
−5.382E-09
2.316E-06
−0.000302
0.0091
0.9725
2700 V
0.001011
1.003
−0.0249
0
0
4.859E-10
−1.814E-07
−9.128E-06
−0.0007
0.9881
14300 V
0.008693
0.999
−0.02
0
−5.043E-11
2.233E-08
−3.046E-06
0.000116
−0.001145
0.9839
VOA
600 V
0.043785
1.04
−0.18
0
0
−4.783E-09
1.962E-06
−0.000229
0.003141
1.092
2700 V
−0.02395
1.006
−0.0188
−1.557E-12
4.556E-10
−4.186E-08
8.346E-07
5.482E-05
−0.003191
0.9729
14300 V
0.005371
1.0102
−0.029
−1.557E-12
4.556E-10
−4.186E-08
8.346E-07
5.482E-05
−0.003191
0.9729
HOA
600 V
0.111147
1.008
−0.24
0
0
−3.895E-09
1.641E-06
−0.000197
0.002615
1.1
2700 V
0.000435
1.006
−0.038
0
0
7.859E-10
−1.914E-07
−9.128E-06
−0.0007
0.9981
14300 V
0.000904
0.999
−0.02
0
0
7.859E-10
−1.914E-07
−9.128E-06
−0.0007
0.9981
Reference:
IEEE 1584-2018
Verify results and send feedback if a discrepancy is found.