Related Resources: Heat Transfer Engineering Design
Heat Loss or Gain From Pipe Excel Spreadsheet Calculator
Heat Transfer Design and Engineering
Download: Heat Loss or Gain From Pipe Excel Spreadsheet Calculator
Calculate the Inside heat transfer coefficient
The formula depends on the flow region
For Laminar flow (Re < 2100) use Sieder and Tate
For this illustration, assume viscosity at wall = bulk viscosity
Laminar flow calculation N/A
For Transition flow (2100 <= Re <= 10000), use Hilpert correlation
It is NOT RECOMMENDED to be in the transitional region, and the correlation is iffy
Transitional flow calculation N/A
For Turbulent flow (Re>10000) use Sieder and Tate (same as Dittus-Boettler, but with viscosity correction)
Turbulent flow calculation 3,440
Note: alternative turbulent flow correlation from Gnielinski
Said to be valid from 3000 < Re < 5,000,000
Because the outside heat transfer coefficient will be so much less than the inside coefficient, it really doesn't make a practical difference if the calculation for inside coefficient is off
Calculate the outside heat transfer coefficient
The outside coefficient is calculated differently for the cases of wind or no wind
No wind = natural convection
Three temperatures to be concerned with, ambient (T4), surface (T3), and average T5 = (T4 + T3)/2
Since T3 is a function of the heat transfer, this is an interative calculation
First, assume a value for T3, the surface temperature
T3_assume
Calculate T5
T5
Get the properties of air for temperature T5
I did a simple linear regression of thermal conductivity for air at atmospheric pressure
MW
P
kair
cair
dair
muair
For no wind condition,
Beta
Gr
Prair
Nuair
Calculation for the case where wind is present
Note that for very low wind velocity (<0.5 m/s), use the greater of this calc or the no-wind calc
Rewind
B
n
Nuwind
Next, calculate the radiation loss
hrad
Add the convection and radiation heat transfer coefficients together
ho
Calculate surface temperatures and iterate until calculation = assumed
Calculate the overall heat transfer coefficient
U
Next, the heat loss through the wall
Q
Calculate the inside wall and surface temperatures based on the estimated surface temperature from above
T3calculated
Calculate the fluid temperature as it exits the pipe segment
Assumes constant properties and constant heat flux along pipe length
For significant temperature changes, divide pipe into segments and calculate sequentially
Cao, Eduardo, Heat Transfer in Process Engineering, McGraw-Hill, 2010
Excel Calculator Credit:
Stephen Hall
