Related Resources: fluid flow
Flash Point Liquids, Gases, Vapors and Solvents
Fluid Engineering and Design
Flash Point of Flammable Gases, Vapors and Solvents
Flash Point of Liquids
A flammable liquid’s vapor pressure and volatility or rate of evaporation determine its ability to form an explosive mixture. These properties can be expressed by the flash point, which is the temperature to which a flammable liquid must be heated to produce a flash when a small flame is passed across the surface of the liquid. Depending on the test methods, either the open- or closed-cup flash point may be listed. The higher the flash point, the more safely the liquid can be handled. Liquids with flash points higher than 100°F are called combustible, whereas those under 100°F are described as flammable. Those with flash points less than 70°F should be regarded as highly flammable.
Table 1.0 Flammable Limits of Some Gases and Vapors
Gas or Vapor
Flash Point,* °F
Flammable Limits, % by Volume
Lower
Upper
Acetone
0
2.5
12.8
Ammonia
Gas
15
28
Benzene (benzol)
12
1.2
7.8
n-Butane
–26
1.9
8.5
Carbon disulfide
–22
1.3
50
Carbon monoxide
Gas
12.5
74
1,2-Dichloroethylene
36
5.6
12.8
Diethylether
–49
1.9
36
Ethyl alcohol
55
3.3
19
Ethylene
Gas
2.7
36
Gasoline
–45
1.4
7.6
Hydrogen
Gas
4.0
75
Hydrogen sulfide
Gas
4.3
44
Isopropyl alcohol
53 .
2.0
12.7
Methyl alcohol
52
6.0
36
Methyl ethyl ketone
16
1.4
11.4
Natural gas (variable)
Gas
3.8 to 6.5
13 to 17
Naphtha
Less than 0
1.1
5.9
Propane
Gas
2.1
9.5
Toluene (toluol)
40
0.1
7.1
o-Xylene
90
0.9
6.7
Table 2.0 . Flash Point Data for Solvents
Chemical Flash Point Boiling Point NFPA Class
° F °C °F °C
Propane (157) (105) (44) (42) IA
Pentane (57) (49) 97 36 IA
Ethyl ether (49) (45) 95 35 IA
Acetaldehyde (38) (39) 69 21 IA
Dimethyl sulfide (36) (38) 99 37 IA
Carbon disulfide (22) (30) 115 46 IB
Ethylene oxide (20) (29) 55 13 IA
n -Hexane (7) (22) 156 69 IB
Acetone (4) (20) 56 133 IA
Cyclohexane (4) (20) 179 81 IB
Tetrahydrofuran 6 (14) 153 67 IB
Benzene 12 (11) 176 80 IB
Triethylamine 20 (7) 193 89 IB
Methyl ethyl ketone (MEK) 25 (4) 176 80 IB
Toluene 40 4 231 111 IB
Methyl alcohol 52 11 149 65 IB
Isopropyl alcohol (IPA) 53 12 180 82 IB
Ethyl alcohol 55 13 173 78 IB
Pyridine 68 20 239–241 116 IB
2-Nitropropane 75 24 248 120 IC
Tert butyl isocyanate 80 27 185–187 85–86 IC
Chlorobenzene 82 28 270 132 IC
Epichlorohydrin 88 31 239–243 115–117 IC
Xylene 81–90 27–32 280–291 138–144 IC
Morpholine 100 38 263 128 II
Acetic acid, glacial 103 39 244 48 II
Bromobenzene 118 48 307–316 153–158 II
Formic acid 122 50 213 101 II
Methyl lactate 135 57 291 144 II
Stoddard solvent 100–140 38–60 300–400 150–200 II
Iso -propyl lactate 140 60 315 157 II
Ethyl lactate 142 61 307 153 IIIA
Benzaldehyde 145 63 352 178 IIIA
Cyclohexanol 154 68 322 161 IIIA
Tetrahydronaphthalene 160 71 406 208 IIIA
Iso -butyl lactate 169 76 360 182 IIIB
Methacrylic acid 170 77 316 158 IIIA
Butyl lactate 174 79 369 187 IIIB
Nitrobenzene 190 88 412 211 IIIA
n -Methyl pyrrolidone 199 93 396 202 IIIA
Benzyl alcohol 213 101 401 205 IIIB
Caproic acid 215 102 400 204 IIIB
Ethylene glycol 232 111 388 198 IIIB
3-Ethyllhexyl lactate 235 113 475 246 IIIB
Phenyl ether 239 115 498 258 IIIB
Stearic acid 385 196 726 386 IIIB
Calculating Flash Points
*Measured by closed-cup method
The following formula allows for the calculation of flash points
1,000 / ( TF undefined +  273 ) = Bo + B1 · log10 · P25
TF = Flash point
Bo and B1 = constant (see table below) P25 = Vapor pressure of liquid at 25°C
This particular calculation is, unfortunately, not very accurate (variation with measured values can be as high as 100°C!) and requires the knowledge of the constants in Table 4-8 as well as the knowledge of the vapor pressure of the compound. Another more simplistic mathematical calculation starts with the autoignition temperature (AIT) in degrees Celsius of the compound . It is shown in Table 2.0 .
Table 3.0 . Constants for flash point calculations . (*These values produce more accurate results and were obtaned by excluding 2,2-dimethylbutane, naphthalene, dodecane, diphenylmethane, tetradecane, nonylbenzene, and decylbenzene.)
Class
Bo
B1
Acetates
2.976
0.380
Acids
2.777
0.491
Alcohols
2.953
0.323
Phenols
2.953
0.323
Aldehydes
2.924
0.443
Alkanes
3.142
0.319
Alkanes*
2.948
0.470
Aromatics
3.142
0.319
Aromatics*
2.948
0.470
Alkenes
3.097
0.424
Amines
3.077
0.322
Esters
2.948
0.385
Ethers
3.056
0.357
Ketones
3.033
0.381
Table 4.0 . Calculations of flash point .
Class
Flash point [°C]
Paraffinic hydrocarbons and olefins in gaseous state at NTP
350 – AIT
Paraffinic hydrocarbons and olefins in liquid state at NTP
250 – AIT
Benzene series
550 – (AIT + K)
Alcohols (MW ≤ 60)
8 + nHr
Alcohols (60 < MW ≤ 88)
11 + 2nHr
Alcohols (MW > 88)
29 + 3nHr
K = a variant (9 for each first branch CH3 and 21 for each second branch CH33 , 16 for each first branch CH and 12 for each second branch CH2)
nHr = number of hydrogen in radicals
Regulatory Requirements Related to Flash Point
Three U.S. government agencies and one private agency have requirements for users of cleaning solvents, based on the flash point of the solvent used. Again, these requirements have at least as much effect on the choice of cleaning solvent as does its solvency power.
These requirements are defined in a classification system which is published in OSHA Standard 1910.106. 38
  • Class IA—Flash Point less than 73 °F (22.7 °C); Boiling Point less than 100 °F (37.8 °C)
  • Class IB—Flash Point less than 73 °F; Boiling Point equal to or greater than 100 °F
  • Class IC—Flash Point equal to or greater than 73 °F, but less than 100 °F
  • Class II—Flash Point equal to or greater than 100 ° F, but less than 140 °F (60 °C)
  • Class IIIA—Flash Point equal to or greater than 140 °F, but less than 200 °F (93.3 °C)
  • Class IIIB—Flash Point equal to or greater than 200 °F
References
  • ASHRAE Handbook of Fundamentals, 2021 Inch-Pound Edition
  • Flash Point Experimental Organic Chemistry, 2016
  • OSHA Standard 1910.106