Related Resources: fluid flow
Appliance Gas Pipe Flow Rate Capacities
HVAC Systems and Components
Fluids Engineering and Design
Appliance Natural Gas Pipe Flow Rate Capacities
Also see: Natural Gas Pipe Flow Rate Requirement Formulas and Calculator for pressure less than 1.5 psig
Piping for natural gas appliances should be of adequate size and installed so that it provides a supply of gas sufficient to meet the maximum demand without undue loss of pressure between the point of supply (the meter) and the appliance. The size of gas pipe required depends on:
(1) maximum gas consumption to be provided,
(2) length of pipe and number of fittings,
(3) allowable pressure loss from the outlet of the meter to the appliance,
(4) specific gravity of the gas.
Gas consumption in ft3/h is obtained by dividing the Btu input rate at which the appliance is operated by the average heating value of the gas in Btu/ft3. Insufficient gas flow in gas supply lines can cause inefficient operation of gas-fired appliances and sometimes create hazardous operations. Gas-fired appliances are normally equipped with a data plate giving information on maximum and/or minimum gas flow requirements or Btu input as well as inlet gas pressure requirements. The local gas utility can give the gas pressure available at the utility’s gas meter. Using this information, the required size of gas piping can be calculated for satisfactory operation of the appliance(s).
The data table given below provides recommended pipe capacities for gas flow for up to 200 ft of pipe based on a specific gravity of 0.60.
Maximum Capacity of Gas Pipe in Cubic Feet per Hour for pipe lengths 10 to 80 ft.
Nominal
Iron Pipe
Size, in.
Internal
Diameter,
in.
Length of Pipe, ft
10
20
30
40
50
60
70
80
1/4
0.364
32
22
18
15
14
12
11
11
3/8
0.493
72
49
40
34
30
27
25
23
1/2
0.622
132
92
73
63
56
50
46
43
3/4
0.824
278
190
152
130
115
105
96
90
1
1.049
520
350
285
245
215
195
180
170
1-1/4
1.380
1,050
730
590
500
440
400
370
350
1-1/2
1.610
1,600
1,100
890
760
670
610
560
530
2
2.067
3,050
2,100
1,650
1,450
1,270
1,150
1,050
990
2-1/2
2.469
4,800
3,300
2,700
2,300
2,000
1,850
1,700
1,600
3
3.068
8,500
5,900
4,700
4,100
3,600
3,250
3,000
2,800
4
4.026
17,500
12,000
9,700
8,300
7,400
6,800
6,200
5,800
Maximum Capacity of Gas Pipe in Cubic Feet per Hour for pipe lengths 90 to 200 ft.
Nominal
Iron Pipe
Size, in.
Internal
Diameter,
in.
Length of Pipe, ft
90
100
125
150
175
200
1/4
0.364
10
9
8
8
7
6
3/8
0.493
22
21
18
17
15
14
1/2
0.622
40
38
34
31
28
26
3/4
0.824
84
79
72
64
59
55
1
1.049
160
150
130
120
110
100
1-1/4
1.380
320
305
275
250
225
210
1-1/2
1.610
490
460
410
380
350
320
2
2.067
930
870
780
710
650
610
2-1/2
2.469
1,500
1,400
1,250
1,130
1,050
980
3
3.068
2,600
2,500
2,200
2,000
1,850
1,700
4
4.026
5,400
5,100
4,500
4,100
3,800
3,500
Note: Capacity is in cubic feet per hour at gas pressures of 0.5 psig or less and pressure drop of 0.3 in. of water; specific gravity = 0.60.
American Gas Association and National Fire Protection Association.