Interpolation Arcing Current Equations and Calculator
Interpolation Equations and Calculator for Arcing Current per IEEE 1584-2018
Reduced Final Arcing Current Equations and Calculator
To determine the final arcing current, incident energy, and arc-flash boundary at a specific voltage, first calculate the intermediate values for the three voltage levels of 600 V, 2700 V, and 14 300 V. Then use the interpolation IEEE 1584-2018 Equation (16) to Equation (18) to determine the final estimated values as follows:
Preview: Interpolation Equations and Calculator for Arcing Current per IEEE 1584-2018
Interpolation Equations for Arcing Current (Iarc)
Interpolation Equation 1 for Arcing Current
Interpolation Equation 2 for Arcing Current
Interpolation Equation 3 for Arcing Current
Iarc_1 = First Iarc interpolation term between 600 V and 2700 V (kA)
Iarc_2 = Second Iarc interpolation term used when Voc is greater than 2700 V (kA)
Iarc_3 = Third Iarc interpolation term used when Voc is less than 2700 V (kA)
Voc = Open-circuit voltage (system voltage) (kV)
When 0.6< Voc ≤ 2.7kV, the final value of arcing current is given as follows:
Iarc = Iarc_3
When Voc > 2.7kV, the final value of arcing current is given as follows:
Iarc = Iarc_2
VCB: Vertical conductors/electrodes inside a metal box/enclosure
VCBB: Vertical conductors/electrodes terminated in an insulating barrier inside a metal box/enclosure
HCB: Horizontal conductors/electrodes inside a metal box/enclosure
VOA: Vertical conductors/electrodes in open air
HOA: Horizontal conductors/electrodes in open air
IEEE 1584-2018