Related Resources: concrete beam shear
Concrete Rectangular Beam Section Analysis Calculator
Beam Deflection Engineering Calculators
Civil Engineering Resources
Concrete Rectangular Beam Section Analysis Calculator Beam or One-Way Type Shear per Per ACI 318-05 Code
RECTANGULAR CONCRETE BEAM/SECTION ANALYSIS
Per ACI 318-05 Code
Input Data:
Beam or Slab Section?
Reinforcing Yield Strength, fy = ksi
Concrete Comp. Strength, f 'c = ksi.
in.
Depth to Tension Reinforcing, d = in.
in.
Ultimate Design Shear, Vu = kips
Ultimate Design Axial Load, Pu = kips
Total Stirrup Area, Av(used) = in.^2
Tie/Stirrup Spacing, s = in.
Results:
fVc =
The ultimate shear strength provided by the concrete, 'fVc', is calculated as follows:
For shear and flexure only (no axial load):
fVc = 2*f*(f'c*1000)^(1/2)*b*d
For shear with axial compression:
fVc = 2*f*(1+Pu/(2*Ag)*(f'c*1000)^(1/2)*b*d
For shear with axial tension:
fVc = 2*f*(1+Pu/(0.5*Ag)*(f'c*1000)^(1/2)*b*d
where: f = 0.75
Ag = b*h
Note: for members such as one-way slabs,
footings, and walls, where minimum shear
reinforcing is not required, if fVc >= Vu
then the section is considered adequate.
For beams, when Vu > fVc/2 , then a
minimum area of shear reinforcement is
required.
fVs =
The ultimate shear strength provided by the shear reinforcing in beams, 'fVs', is calculated as follows:
fVs = f*fy*d*Av/s2
where: f = 0.75
The required amount of shear strength to be provided by the shear reinforcing in beams is:
fVs(req'd) = Vu-fVc >= 0.
The required amount of shear strength to be provided must be <= fVs(max).
kips
fVn = fVc+fVs =
fVs(max) =
The maximum allowable ultimate shear strength to be provided by the shear reinforcing in beams, 'fVs(max)', is calculated as follows:
fVs(max) <= 8*f*(f'c*1000)^(1/2)*b*d/1000
where:
f = 0.75
Av(prov) = in.^2  = Av(used)
Av(req'd) =
The required area of shear reinforcing, 'Av', perpendicular to axis of the beam is calculated as follows:
Av = fVs*s/(f*fy*d) >= Av(min)
where:
f = 0.75
fVs = max. of: (Vu - fVc) or 0
Note: Av = area of both legs of a closed stirrup.
Av(min) =
The minimum area of shear reinforcing, 'Av(min)', to be provided for beams is calculated as follows:
Av(min) = 75*SQRT(f'c*1000)*b*s/fy
but not less than: 50*b*s/(fy*1000)
Note: Av(min) = area of both legs of a closed stirrup.
s(max) =
The maximum allowable shear reinforcing (closed stirrup) spacing, 's', shall not exceed d/2, nor 24". However, when fVs > 4*f*(f'c*1000)^(1/2)*b*d, then the maximum spacing given above shall be reduced by one-half. (Note: f = 0.75)